Hello everyone. I'm new to the forum. I have a problem with the encoder and PID. We need to turn an encoder controlled rollover. I am using s7-1500 tia portal v15.1. We have to slow down the speed of the engine during the first starts and stops. In other words, it will stay slow and accelerate, after going at a constant speed, it will slow down near the end. how can I do that.?šŸ™ƒ
 
More information is required for example what is the drive ? I assume it will be a VFD type as you are using an analogue why a PID ? etc.
The first thing that comes to mind is set the PID to manual with a fixed speed on the start command, then after a time or number of encoder pulses ramp to the required speed (if PID switch PID to auto) then when within say 10% of travel switch back to Manual PID with a fixed speed.
Never done it with a PID but done many VFD drives for positioning in that mode it is just a case of setting the analogue output to a pre-set low speed, after so many pulses from the encoder set analogue to required speed and the same at the end of travel.
 

Similar Topics

Does a solid state soft starter have a DC Buss / DC Buss voltage like a VFD does?
Replies
1
Views
255
Haven't done much with soft starts, more-so VFDs' in my time. Looking at replacing 3 x 37KW (415 V 50 Hz) star-delta starters with soft starters...
Replies
11
Views
2,878
Is there a way to get the fault history from a SIRIUS 3RW4456 Soft Start through the HMI keypad? I've been through the manual but it is pretty...
Replies
0
Views
748
We are going to be using a SIRUS 3RW5545 Soft Start to control a 480V, 150HP fan. Looking for some recommendations for parameters to use with this...
Replies
0
Views
852
Good Morning , We have a 100 HP , 480 V (Full Load Amps 124 ) Hammer Mill motor that has a Wye/Delta starting procedure. I would like to put...
Replies
16
Views
4,256