@sbaum.
+1 that a softstarter with bypass will be unaffected by the current peaks after startup.
If the softstarter does not have an integral bypass contactor, one can be added outside the VFD.

@Cydog.
The extra high starting current will heat up both motor and electronics.
Because of that , both starting frequency and starting class must be taken into account when sizing both motors and electronics.

Softstarters do not have a DC stage with capacitors like a VFD.
 
Thanks . That makes sense . If you don't mind , I have one more question .
This motor is a 125 HP and the full load amps are 156 amps . How much larger would you go , oversizing the soft start for this 125 HP Pellet Mill motor , in case feed is left in the Pellet Mill ? 150 HP , 200 Hp , ? Of course we don't want to break anything .

Thanks again
 

Similar Topics

Hello, I have a question about fuses and how to calculate their required size. I understand that determining the appropriate fuse size isn't...
Replies
0
Views
180
Specification of Codesys is being driven by customer and I'm being asked to control roughly 100 network connected vfd's for a conveying project in...
Replies
12
Views
3,227
I have 120 VAC feeding a Micrologix PLC. I am feeding my I/O with 24 VDC using a power supply. If I add up the current draw of all I/O, I get 5...
Replies
14
Views
4,745
Hello! I have a question regarding the HMI in InTouch, almost a month ago I made an HMI and I have not used it again, now I need to make changes...
Replies
6
Views
2,102
Sorry, not really PLC's. I have been going around and around trying to get a solid answer to my question and not finding anything that really...
Replies
15
Views
4,984
Back
Top Bottom