jkerekes Member Join Date Aug 2007 Location NJ Posts 2,363 Sep 6, 2023 #1 Studio 5000 version 34. Have error on PIDE CVFaulted (Status1.2), Control variable (CV) health bad. No more information online or in instruction manual. What could be some of the causes of this error. Thanks.
Studio 5000 version 34. Have error on PIDE CVFaulted (Status1.2), Control variable (CV) health bad. No more information online or in instruction manual. What could be some of the causes of this error. Thanks.
tlf30 Lifetime Supporting Member Join Date Apr 2021 Location Deadhorse Alaska Posts 206 Sep 6, 2023 #2 Sounds like the CVFault input is set to true, is something writing to it?
jkerekes Member OP Join Date Aug 2007 Location NJ Posts 2,363 Sep 6, 2023 #3 I’ll check that tomorrow. I missed that. Does the status1.2 bit prevent the PIDE from going into Auto mode?
I’ll check that tomorrow. I missed that. Does the status1.2 bit prevent the PIDE from going into Auto mode?
tlf30 Lifetime Supporting Member Join Date Apr 2021 Location Deadhorse Alaska Posts 206 Sep 7, 2023 #4 I just tested on the bench, setting the CVFault will force the controller to manual.