Consumed/Produced Tags between 1756-L55 & L71

lrahman

Member
Join Date
Oct 2017
Location
Dubai
Posts
21
Sir,
I have installed 1756-L55 Controller in slot-0 and L71 Controller in slot-1 of Control Logix 13 slot chassis. i can read data from L55 in L71 project via produce/consume tags concept but reverse is not happening. i cannot add L71 controller in L55 project's IO configuration. Please advise any firmware upgrade for L55 or firmware downgrade for L71 to have read/write data access between these two Controllers. Thanks.
 
Put your L71 into the L55's I/O configuration as an L63 for L55 F/W up to 15, or an L64 for F/W 16.

It will work, as nothing has changed in the Producer/Consumer model ....

EDIT : I am certain I have done this myself a couple of years ago, but I can't check as I only have an L55, an L61, and an L63


EDIT2 : Electronic Keying is not relevant to Controllers, so there should be no "I/O" errors. So long as the producer produces, consumers can consume....
 
Last edited:
Put your L71 into the L55's I/O configuration as an L63 for L55 F/W up to 15, or an L64 for F/W 16.

It will work, as nothing has changed in the Producer/Consumer model ....

EDIT : I am certain I have done this myself a couple of years ago, but I can't check as I only have an L55, an L61, and an L63


EDIT2 : Electronic Keying is not relevant to Controllers, so there should be no "I/O" errors. So long as the producer produces, consumers can consume....



Thank you sir I upgraded L55 FW to 16 and added L64 as disguise for L71 its working fine thank you.
 
I know this thread is old but I had to. You're a lifesaver, been struggling for over a week trying to get these controllers to communicate. This worked like a charm
 

Similar Topics

Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
Replies
2
Views
174
Hi I have been knocking my head against the wall trying to figure out why these two plcs won't talk with Produced and Consumed Tags data. The...
Replies
14
Views
480
Hello all. I have a 1769-L16 that I inserted a 1769-L35E into. I was expecting it to create module defined tags automatically in my controller...
Replies
10
Views
1,816
Hi, Can a tag configured as a Produced or Consumed tag be read or written to with Explicit Messaging? Context: we are retrofitting an AV system...
Replies
9
Views
2,255
Ok, I've setup comms to PLC's that are behind a NAT switch before, but I have not had a PLC behind one NAT switch communicate with a second PLC...
Replies
13
Views
3,436
Back
Top Bottom