Is it possible to increase the area that retentive %MW registers reside.
Aka, is it possible to address them at %MW4096 and above w/ a software change?
 
The manual says it has 16kB of retentive data.
It also says on page 90 how you can set it all to flags,
"The breakdown of the NOVRAM can be modified when required in the
programming software WAGO-I/O-PRO/Register "Resources"/Dialog window
"Target system settings"."

You should be able to get to %MW8191
 
Thanks for your reply.
I read the help.
I even pulled up that section of the manual.
So, it seems like it is possible to use all 16kB of retentive data for located data (aka flags, aka new term for me).
As all my retentive data is located, and that would allow me to use this particular plc possible, it seems like a no brainer.
Unfortunately, I can't seem to figure out how to do this.
And the lady at wago tech support just replies w/ "I feel that you shouldn't change the settings from default"
ug
 
Under PLC configuration you can find the settings for all the registers and such.
I would change the numbers (save the old settings first someplace, screenshot maybe) and change the HEX numbers such as 4000 to 0000 or a different number, see what happens, it may actually free up the registers/memory set aside as ret to regular use.
You may end up with a brick for all I know but worth a try?
 
I wish I knew how to make the 16kB memory available.
Based off of responses, it seems possible.
I managed to increase the 16kB retentive memory, but I haven't figure out how to make all 16kB memory addressable.
Does anyone out there know if this is possible?
Or am I heading down a rabbit hole.
 
Last edited:
This is from an older 750-841.
Stock config.
You could change the memory assignment to extend the range.
Not sure what you may have changed so far.

Wago_Mem.jpg
 
the retain %MW is what I need to increase. So, I am going to take your advice and set the retain start to 16#20004000 and see if that does it.
 
did not work

the %MW located data range for the retain area is fixed and can not be changed.
Now for the good news.
The codesys software was limiting the range to 4096.
That was the range for the 750-852.
The 750-862 is 0- %MW12,287.
I just need to upgraded my software to let it recognize this.
 

Similar Topics

Hello, I m having a problem with wago 750-862 plc. The plc won't start automatically in run mode after a power reboot. I've also tried the...
Replies
4
Views
422
Does anyone know how to set the time and date programmatically in the wago 750-862? Or direct me to the library that I need & link? I am using...
Replies
2
Views
1,650
I know someone out there has code to programmatically set the plc time and date. It would save me a ton of time if anyone could share this w/ me...
Replies
4
Views
2,744
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
104
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
141
Back
Top Bottom