We are thinking of implementing a light to our safety system that indicates that a machine is in a ceratian more dangerous state then normal.

Talking to a safety specialist he said (but didn't know how to) that maybe I could have an indication if the light was broken. For example a relay is activated when the indication light is broken.

I can't figure out how to achieve this. Also I don't know HOW the indication light behave if it's broken. Does it still have the same internal resistance? Is it lower, higher or zero. It seems that he took this out of thin air without knowing there is a solution for it.

/Tim
 
Make it so the led is on when it is not more dangerous, if the LED fails then it indicates a more dangerous state than normal. Make it an illuminated pushbutton so you press it to test the LED.
 
Make it so the led is on when it is not more dangerous, if the LED fails then it indicates a more dangerous state than normal. Make it an illuminated pushbutton so you press it to test the LED.

I would say that the "norm" is to have my flashing light indicate a more dangerous state. A non-lit light is not a good way to inform of a more dangerous state in my opinion since it does not catch the eye or make you aware that something is as it shouldn't be.

I could have two light, but then I would depend on that the faulty light is fixed before the other fails

/Tim
 
Perhaps an acceptable approach would be to have redundant LED lights and include a testing feature. Then have instructions that an operator or maintenance person must verify the operation of the lights periodically.

I have also seen a lot of safety circuits specify that they be supplied by SIL rated power supplies and include a specific overcurrent rated device.
 
The traffic light people already solved this by monitoring the current going to the lamp. That's one way of doing it, though if it's an LED it will be tricky I think.
 
Thanks!
I now have two approaches.
I found a relay from Schneider Electric RM35JA31MW that was an under/overcurrent relay, seems to fit my need. Also the redundant lights are an option
/Tim
 
I've heard of applications before where LED indicators were specified to have transistor feedback to show they were energised. I wonder if a faulty LED would be detected on the dark test from the failsafe IO though?
 
I recall having seen many years ago a special output board that had a resistance and that resistance was used to measure if the light (bulb o led) at the end was ok or not. That was on Allen Bradley.
 
we use AB safety gate locks and use the LOTO method.
the gate lock cannot be closed when a lock is on and the machine safety logic will not allow the machine to run without the gate lock being reset.
Can you do something like that?
james
 
The lamp and lower safety level is achieved with a key switch and a contactor relay (rated PLc).

In this safety level the machine can run with the lids open but only at 15% speed, this is what I want to indicate. As soon as the key switch is turned the light will flash indicating that IF the lids are open the machine can still turn at 15% speed. So I can't use any locks.

I appreciate the output modules examples but we use Siemens and the safety functions doesn't go through a PLC.
 

Similar Topics

My apologies if it is something to basic or simple, but I'm pretty sure the 'Verify controller' button in RSlogix 5000 was always on i.e. I could...
Replies
1
Views
2,111
First off, I'm a hobbyist-level programmer, and this program isn't controlling anything anything that could even remotely be considered "life...
Replies
18
Views
647
Hi, I'm working on a project with an Allen-Bradley PLC, so we are using Studio5000. I have a bunch of things that communicate through ethernet/Ip...
Replies
2
Views
1,264
I've created an AOI in Studio 5000 for the first time. This is an AOI to do a bunch of math to calculate air properties. I don't have access to...
Replies
25
Views
5,552
Does anyone know what “DT Errors” mean when verifying a program after downloading in Ladder Logistixs software?
Replies
6
Views
2,543
Back
Top Bottom