Upgrading an old SLC line to CLX / safety

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,046
I'm quoting a big line upgrade that currently has a L55 and 7 SLC 5/01 processors, all of which are islands. I plan to change to an L71S and my original intention was to use PointIO in the SLC cabinets (there are only 3-4 modules in each cabinet) and to use Guard IO so it can all be controlled from the GuardLogix. However, all the IO in the remote cabinets is 120vac and it doesn't look like there are any 120vac Guard IO modules, so I'm considering the 440C Guardmaster in conjunction with the regular PointIO modules. Replacing all of the existing motor starters with 24vdc coils is out of the budget for this job.
Does anyone have another suggestions that I'm not seeing?
 
Use terminal mounted isolation relays. I do that almost all of the time for outputs (24 VDC Driver for 120 VAC output), and sometimes for inputs. No reason you can't.
 
Keep in mind that in order for force-guided relays (aka "safety relays") to be effective, the normally closed auxiliary contact needs to be used as an EDM circuit back to the controlling safety device. There is nothing special about these relays except that the contacts are mechanically linked so you can detect a welded contact by monitoring the NC pole. If this is not done then the safety relay offers no advantage over a general purpose relay.
 
Keep in mind that in order for force-guided relays (aka "safety relays") to be effective, the normally closed auxiliary contact needs to be used as an EDM circuit back to the controlling safety device. There is nothing special about these relays except that the contacts are mechanically linked so you can detect a welded contact by monitoring the NC pole. If this is not done then the safety relay offers no advantage over a general purpose relay.

Makes perfect sense. Thanks.
 
And that will meet safety requirements?

It is hard to say.

We don't have any data on your safety requirements.

My initial thought is if you are replacing SLC5/01 I/O then your requirements aren't very high. Likewise if the motors starters do not include safety contactors, then safety relays to pull in the contactors are probably not needed either.

However, if you intend to raise the level of safety required in this upgrade, you will need to evaluate how you will meet those requirements.

You can't just throw "safety" hardware at everything and it will be ok.
 
It is hard to say.

We don't have any data on your safety requirements.

My initial thought is if you are replacing SLC5/01 I/O then your requirements aren't very high. Likewise if the motors starters do not include safety contactors, then safety relays to pull in the contactors are probably not needed either.

However, if you intend to raise the level of safety required in this upgrade, you will need to evaluate how you will meet those requirements.

You can't just throw "safety" hardware at everything and it will be ok.

I knew this reply would come :D. I was referring to safety levels along the lines of GuardLogix and Guard I/O control. The previous responses were just what I needed. Safety relay with monitoring feedback is perfect. The existing system, I believe, uses standard relays to drop out the starters. They currently have a keyed bypass switch to bypass numerous safety components, so this is a much needed upgrade.

On another note, is there a reason they have limited Guard I/O modules? I am still surprised that there are no 1756 modules.
 
Safety relay with monitoring feedback is perfect. The existing system, I believe, uses standard relays to drop out the starters. They currently have a keyed bypass switch to bypass numerous safety components, so this is a much needed upgrade.

I might be misunderstanding but it sounds like you are planning on using force-guided relays to control the existing starters which act as your final disconnecting means. Assuming your using Guardlogix because you need to meet SIL 3 (ControlLogix can support up to SIL 2). Unless the existing starters have force-guided contacts I doubt that you will be able to meet your safety requirements as you must have feedback from your interposing relay as well as the final output contactor.
 

Similar Topics

Hi, I am upgrading a Wonderware SCADA form version 9.5 to version 23. I am able to migrate all the graphic, but when to activate the runtime this...
Replies
8
Views
508
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
Replies
5
Views
586
I am looking to upgrade some of our old Servo Drives to the newer kinetix 5700 style. currently we have 4 1394 axis that are all driven by 5kw...
Replies
1
Views
915
Hello, We are currently running a bunch of g310's connected to their SLC5 PLCs through ethernet. I've attempted to upgrade the program from 2.0...
Replies
1
Views
1,156
Hello everyone, My company has an old line for building DC motors. Many machines are from the early 90's and some requests for safety...
Replies
2
Views
1,179
Back