adrirock1141
Member
Hello Everyone i got a problem with Endress Hauser FlowMeter Promag W400, in his specification says it support Ethernet/IP protocol (https://www.endress.com/en/field-in...ter-promag-w400-5w4c?t.tabId=product-overview)
this Flowmeter has a Integrated WebServer, in this webserver i configure the Flowmeter IP in the WebServer, this are de List IP
Flowmeter
IP:192.168.0.25
Subnet:255.255.255.0
Gateway:192.168.0.10
PLC
IP:192.168.0.13
Subnet:255.255.255.0
Gateway:.....
PC
IP:192.168.0.113
Subnet:255.255.255.0
Gateway:192.168.0.10
I can ping the flowmeter, and i can connect to the webserver trough the chrome navigator
I also install de AOP file from Endress Hauser Website, and the EDS file in the EDS file tool in Rslogix5000, but i cant find the flowmeter in rslinx and also when i add the flowmeter in Rslogix5000 i cant connect to the PLC there is a symbol of danger in the flowmeter in Rslogix, i dont know if it is necesary to configure something else, please help!!!!
this Flowmeter has a Integrated WebServer, in this webserver i configure the Flowmeter IP in the WebServer, this are de List IP
Flowmeter
IP:192.168.0.25
Subnet:255.255.255.0
Gateway:192.168.0.10
PLC
IP:192.168.0.13
Subnet:255.255.255.0
Gateway:.....
PC
IP:192.168.0.113
Subnet:255.255.255.0
Gateway:192.168.0.10
I can ping the flowmeter, and i can connect to the webserver trough the chrome navigator
I also install de AOP file from Endress Hauser Website, and the EDS file in the EDS file tool in Rslogix5000, but i cant find the flowmeter in rslinx and also when i add the flowmeter in Rslogix5000 i cant connect to the PLC there is a symbol of danger in the flowmeter in Rslogix, i dont know if it is necesary to configure something else, please help!!!!
Last edited: