Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400
Messaging but don't see the N files in the 525 manual. I do see in the 525 manual that some of the
things like speed control would be 600 in a 40P for 60 hz while the 525 it would be 6000 for 60 hz
 
If this is your 1st dance with the ML1400/PF525 combination over the Embedded Ethernet port on the PF525, pay particular attention to N42:3.
Page 136 has comments about this:

PG 136.jpg

This next pic is a MSG dealing with N42:3

MSG.png

If you do not have this message set up, nothing will work.


This can easily be accomplished with an automatic trigger of the message:

Auto trigger.jpg


I got the automatic trigger from Rockwell Sample Code, quite a while back, and it works quite well. Never an issue.

I am not sure if you can set N42:3 to a non-zero number other ways, but this is what I have, and it works well.
 
Last edited:
Thanks for the update, just got the email, I managed to find the first screenshot you sent in another manual one 525, looks the same as
setting up a 22 E-COMM on a 40P . I wont get to test one for a while as I am other projects, but wanted to get my cookie cutter
program written with the comm's and messaging. I will have to check if you can set them up on the network with CCW like the 40P
I would suspect you can. Thanks..
 

Similar Topics

I'm in the process of replacing an existing powerflex 40p. The old one died with no software backup but we did have a printout of the parameters...
Replies
3
Views
1,209
How can I find the IP of a used Powerflex 40p? I have used them in the past I have a hand held programmer for the 22 Comm E that I used before...
Replies
4
Views
1,762
Is there a way in rsnetworx or connected components to compare 2 powerflex parameter sets? TIA P.S this is also my first post here so hello...
Replies
5
Views
2,219
I have P036 configured as 2 wire SRC Control with an exteranl supply. I choose the direction with a 3 point rotary switch. The problem is when it...
Replies
1
Views
1,161
Hello all. Been reading for a long time, 1st real post. AB was unable to help me beyond "Yeah, that's old, we think you should upgrade..." which...
Replies
4
Views
2,388
Back
Top Bottom