Hello all,

I have a MicroLogix 1100 Series B that I am trying to read data from and into a PLC-5/20 Series D Rev A.

I assume this is possible, but I have an additional piece of hardware that might be tripping me up. The 1100 connects via Ethernet to a DataLink GW1000-ABEIP protocol converter. From there, we go DH+ to the PLC-5. This is all existing equipment and wiring and I am really just trying to pull data from the 1100 into the PLC-5. I have not taken a look at the configuration of the GW1000, so I do not know if it has any parameters that would need to be changed in this case.

I configured a MSG instruction in the PLC-5, as follows:

This PLC-5:
Communications Command: PLC-5 Typed Read
Data Table Address: N7:20
Size in Elements: 8

Target Device:
Data Table Address: N7:10
Local Station Address (oct): 7
Local/Remote: Local

The converter is the actual device on the DH+ network (not the 1100) and has DH+ node address 07. Could it be that the PLC-5 cannot "see" through the converter to pull the requested data? Or, do I have my messaging jumbled up somehow?


Thanks in advance for any pointers!

Justin
 
I was reading over the MSG instruction help and came across the following:

"Using the MG control block, the control block size is fixed at 56 words. You must use the MG control block if you are sending messages to an SLC 500 processor using the SLC read and write commands, or if you are sending messages out any other port than channel 1A."

It would seem that I should be using the MG control word, with a "PLC-5 Typed Read to SLC," as opposed to an Integer control word. Can anyone confirm this? I am going to give it a shot when I am onsite again, but if anyone has additional suggestions, I would appreciate it.


Thanks,

Justin
 

Similar Topics

I'm trying to MSG from a SLC 5/05 to read a single INT from a PLC-5. I can't for the life of me get it to work! SLC Ch1 Config RsLinx...
Replies
6
Views
5,769
I am trying to read data from a PLC-5 in my ControlLogix program over Ethernet. I keep getting a connection failure. I followed this procedure...
Replies
14
Views
20,844
I have a network with 4 PLCs PLC1 is controllogix and PLCs 2-4 are compactlogix and they all need to communicate. The current way I have this...
Replies
8
Views
296
Hello All, is there any way to fetch remote controllers Mode Run/Remote Prog/Faulted etc. ( AB L8 Series) using CIP message, if yes please share...
Replies
5
Views
838
Hello all. Working on a centrifuge for a customer. They have ACS880 ABB Vfd's installed, and need them to talk VIA the FENA card Ethernet to...
Replies
1
Views
1,359
Back
Top Bottom