Hi,

Is it possible to write tag using MSG in two diffirent controllers in separated networks using Dual-IP? I need to do something like that:

1. My PLC L320ERM[10.38.101.1(SUB:255.255.0.0)] Port 1 --> L350ERM[10.38.100.1]
2. My PLC L320ERM[192.168.2.1(SUB:255.255.0.0)] Port 2 --> 1768-L45[192.168.1.100]

So far I am using Linear/DLR configuration and connection no.1 is working. Now I need to add second connection.

Another problem is, when I try to add L45 CPU in ethernet tree I cannot find it (probably very old?)
 
You don’t need an object in the tree to message it. Since you’re in dual IP mode, off the top of my head, the message path for the A1 port would be “3, 10.38.100.1“. If you use A2, it’s “4, 192.168.1.100“.

In DLR mode, you’d also be issuing messages containing different IPs, but same interface number. Identical format to how messages would be sent using a 5370:
- “2, 10.38.100.1”
- “2, 192.168.1.100”

A route needs to exist between networks.
 
Last edited:

Similar Topics

I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
126
Hi all I'm trying to setup a MSG connection (which I'm not familiar to) between a CompactLogix CPU (L310ER) and a Micrologix 1400 CPU. At the...
Replies
1
Views
818
Anyone know if I can msg between a ControlLogix L71 (A) and an SLC5/05 (C) via backplane of second ControlLogix L71 (B)? ControlLogix (A) and SLC...
Replies
4
Views
2,736
Hey everyone, I feel like this is an easy question, but I can't seem to find an answer for it. Currently have a PLC-5 that we're swapping out...
Replies
3
Views
1,848
Hello, I am trying to msg between a 1756-ENBT and a 1756-ENBT. One PLC is on a 192.168.34.xx subnet with a 1756-ENBT in slot 2 with a...
Replies
11
Views
2,686
Back
Top Bottom