Micrologix1400 and IF4 getting an odd error condition

jay mason

Member
Join Date
Oct 2013
Location
Easton Pa
Posts
4
I have a an issue with a micrologix 1400 control system with a 1762 if4 analog card.
I have 3 devices connected to the analog card one 0 to 10 vdc. and 2, 4-20ma transducers
For some reason the 0-10 volt signal which is a strain gauge amplifier is showing saturation on my HMI and shuts down the system but not the other two signals are fine.
If I power down and back up this clears the fault and all is fine for a day or so then I get the same fault the analog card shows 32768 as the counts which would be saturation.
Is there a reason the micrologix would retain the saturated condition?
Thanks
Jay
 
jay,

Several things come to mind.

1. has the program changed in regards to the analog input and math?
check your math statements.
2. load cell amplifier is going bad.
3. load cell is going bad. Happens more often than you think. we replace 10-20 a month. 10k to 200k in size.
4. have you checked the wiring? is the wiring shielded and grounded in only one location?

you may want to consider unlatching the math overflow / underflow bit in the last rung of your program to prevent the plc from faulting out.

regards,
james
 

Similar Topics

Hi All I have a Panelview 800 HMI hooked up to a Micrologix 1400 controller. I have communication and have the screen set up with some...
Replies
1
Views
945
I have tried to find this everywhere and I am really not sure what I am doing wrong. I am trying to use a CompactLogix and the message functions...
Replies
10
Views
2,835
Hi Friends, I am trying to connect MLX1400 over RS232 serial communication with PV800. I am not sure where I am going wrong, the PV800 doesn't...
Replies
6
Views
971
Hi Friends, I have been away from PLC systems for a while and was more in to BMS. However, recently I started working on a new project where we...
Replies
2
Views
790
Is there anyway to be certain that the memory module in a ML1400 has been written to with the current program? I have controllers in the field...
Replies
0
Views
874
Back