Hi, Everyone

I am interfacing rotary encoder(incremental encoder) with PLC. This encoder using for speed measurement (RPM). The encoder is giving pulses which reading is not stabilised for every rotation of same speed. it is fluctuating 0 to 5 pulses which results to variable readings.
For this problem, I have done following things..
1. Encoder wire shield is connected to earthing.
2. Separate encoder wire routing.
3. Averaged the encoder reading pulses in PLC program
4. Find max value program of encoder pulses in PLC.

But, still it has variable reading. Kindly help me out.

PLC- Siemens ST20-smart
Encoder : Delta ES3- 360PPR

Regards
Nilesh
 
What is your encoder on?
How is it coupled to the load?
99% of the time, if the encoder is fluctuating, so is your speed.

Encoder is connected to conveyor which carried by a oriental make three phase induction motor around 150-220 watt(3-Phase 240 VAC).
 
How is the coupling done?

8/10 times, the coupling is loose or broken.

1/10 times, the coupling is not flexible and is at an angle causing a wobble that is visible in the encoder readings.
 
How is the coupling done?

8/10 times, the coupling is loose or broken.

1/10 times, the coupling is not flexible and is at an angle causing a wobble that is visible in the encoder readings.

I asked same thing with mechanical person and checked. Remaining flexibility only we can assume that it is OK.

I want to find this solution through software logic...
 
Define the actual problem. You aren't going to get servo like speed control from a conveyor. What are your real (and not wishful) requirements ?

The speed WILL actually change as loading changes, that is normal.
 

Similar Topics

Hi guys! I know the Siemens S7-1200 has pulse inputs but I was wondering if you can connect a standard incremental encoder in quadrature mode...
Replies
3
Views
4,032
Hi. I'm a begginer with the PLC staff. Could you please show me an example program /with a scheme/ for a simple project using a rotary encoder...
Replies
5
Views
7,974
Hi, I am working on a project to upgrade a control cabinet for assembly machine. We are thinking also to replace some CAM_SWITCHES with OMRON...
Replies
12
Views
9,197
Hello, I am working with a omron E6C2-CWZ5B rotary encoder (differential phase A, B and Z, 360 P/R). I am having trouble with it finding degrees...
Replies
5
Views
3,379
Dear team, We are constantly facing M07 incremental loss on one of our kinetix 6500 safe torque. We have changed Servo motor (MPL-B4530K-MJ72AA)...
Replies
1
Views
146
Back
Top Bottom