Client has multiple spare Panelview 550 (2711-T5A10 L1 PV550 Touch Devicenet)
https://www.plctalk.net/qanda/attachment.php?attachmentid=67576&stc=1&d=1703214624
I have finally been able to get a copy and a serial for Panelbuilder 32 (3.83.01)
Was able to upload from a Panelview 300 Micro (2711-M3A18L1 PV300 Micro Keypad DF1)
2 issues, issue 1:
Converted the terminal setup from the 300 to the 550, however getting a lot of tag errors.
https://www.plctalk.net/qanda/attachment.php?attachmentid=67577&stc=1&d=1703214624
Issue 2:
I haven't been able to conect to the device to even download a blank project.
I've asked a uni friend that has worked at Rockwell Automationand we still couldn't connect on.
We have tried using RSLinx DF1, and also tried disabling the printer port on the PV550 and make sure the connection is deleted from RSLinx and closed.
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/2711-um014_-en-p.pdf
I haven't tried, but can I connect to the HMI through the PLC DF1 connection if the PLC has a 1769-SDN?
PLC is a 1764 Micrologix 1500 LSP Series C.
I can test this on when back site in early January as site is closed from today.
Any help would be apreciated.
https://www.plctalk.net/qanda/attachment.php?attachmentid=67576&stc=1&d=1703214624
I have finally been able to get a copy and a serial for Panelbuilder 32 (3.83.01)
Was able to upload from a Panelview 300 Micro (2711-M3A18L1 PV300 Micro Keypad DF1)
2 issues, issue 1:
Converted the terminal setup from the 300 to the 550, however getting a lot of tag errors.
https://www.plctalk.net/qanda/attachment.php?attachmentid=67577&stc=1&d=1703214624
Issue 2:
I haven't been able to conect to the device to even download a blank project.
I've asked a uni friend that has worked at Rockwell Automationand we still couldn't connect on.
We have tried using RSLinx DF1, and also tried disabling the printer port on the PV550 and make sure the connection is deleted from RSLinx and closed.
Summary
PanelView Standard: Application transferring via serial port
Question
How can I download/upload application to/from the PanelView Standard thru the RS-232 port?
How can I download the application to the PanelView Standard with a DH+ and printerport RS-232 like the 2711-K10C8?
Note
: We need to disable the printer port for printing before we can perform the download.
Note:
If you are transferring the application thru the Point-to-Point driver, you must delete the RSLinx Classic DF1driver, or close and shutdown RSLinx Classic.
If you are using the RSLinx Classic driver for serial communications, set it as:
RS-232 DF1 devices
Comm Port: set COM1 for DB9 connector, set other COM for USB converter.
Device: SLC-CH0/Micro/Panelview
Baud rate: 19200
Parity: None
Stop Bits: 1
Error Checking: CRC
Protocol: Full Duplex
Refer to
PanelBuilder32 Software Getting Results
, Publication 2711-GR003.
PanelView Standard: Application transferring via serial port
Question
How can I download/upload application to/from the PanelView Standard thru the RS-232 port?
How can I download the application to the PanelView Standard with a DH+ and printerport RS-232 like the 2711-K10C8?
Note
: We need to disable the printer port for printing before we can perform the download.
Note:
If you are transferring the application thru the Point-to-Point driver, you must delete the RSLinx Classic DF1driver, or close and shutdown RSLinx Classic.
If you are using the RSLinx Classic driver for serial communications, set it as:
RS-232 DF1 devices
Comm Port: set COM1 for DB9 connector, set other COM for USB converter.
Device: SLC-CH0/Micro/Panelview
Baud rate: 19200
Parity: None
Stop Bits: 1
Error Checking: CRC
Protocol: Full Duplex
Refer to
PanelBuilder32 Software Getting Results
, Publication 2711-GR003.
I haven't tried, but can I connect to the HMI through the PLC DF1 connection if the PLC has a 1769-SDN?
PLC is a 1764 Micrologix 1500 LSP Series C.
I can test this on when back site in early January as site is closed from today.
Any help would be apreciated.