ge fanus 90 30 comm problem

johnplouffe

Member
Join Date
Dec 2006
Location
rhode island
Posts
2
i have a ge 90 30 plc and cant get it to comm with the lap top .The lap top is only used for plcs and has been used for this plc .it is the dos version program and the com port on the computer is fine.Ordered a new cable for connection and tried two differenrt cables .probably a setting problem
 
Do you use the laptop to communicate with any other PLCs? Sometimes the communications drivers have to be manually turned off or they don't relinquish the COM port for other applications. GE Fanuc PLCs and Logicmaster software both default to the same COM port settings and rarely have to be changed.
 
What are you using for a cable? The port on the 90-30 power supply is RS-485. Most people use a a converter to go from RS-485 to RS-232, although RussB and others have posted the pinouts for this "cheater" cable that works without any converter.


9 pin 15 pin-M

Rd 2 --------------- 12 SD+(B)

Td 3 --------------- 10 RD+(B')

Sig.Gnd. 5 ---------------- 7 SG

RTS 7 ---| |--- 6 RTS+(B)
| |
CTS 8 ---| |--- 15 CTS+(B')

DTR 4 ---| |--- 8 CTS-(A')
| |
DSR 6 ---| |--- 14 RTS-(A)

 

Similar Topics

I am replacing older GE series 6 PLC with ControlLogix. I have over 2000 rungs of ladder logic to convert! :hmmm: Is there a converting software...
Replies
4
Views
6,834
Hey guys. As the title suggests, I need to configure a Danfoss Aquadrive FC202 inverter, so that its logic inhibits the local command when the...
Replies
2
Views
48
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
Replies
16
Views
505
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
Replies
1
Views
137
Guys need a bit of help getting the instance correct for a 22comme with a PF40P. Trying to get 2 things first is the drive current amp draw...
Replies
1
Views
93
Back
Top Bottom