Maybe someone here can help me or tell me this isn't possible.
I have two CLX L71 processors with one HMI. They are for two slicers that are part of the same system but they can be turned off independently for maintenance. Each one is messaging (identical messages) to get status from downstream equipment.
What I would like to do on the HMI (PVPlus 6) is display the information from slicer one but if the comms are lost then hide the panel of multistate indicators and display the identical information from slicer two. I have tried setting visibility something like this "If ({[CLX1]@Status}) = "ok" Then 1 Else 0" but it goes wire frame when the communications are lost.
Is there any way to do this with ME or would I be better off using slicer one to monitor slicer two and vice versa, then control visibility from the opposite controller?
I have two CLX L71 processors with one HMI. They are for two slicers that are part of the same system but they can be turned off independently for maintenance. Each one is messaging (identical messages) to get status from downstream equipment.
What I would like to do on the HMI (PVPlus 6) is display the information from slicer one but if the comms are lost then hide the panel of multistate indicators and display the identical information from slicer two. I have tried setting visibility something like this "If ({[CLX1]@Status}) = "ok" Then 1 Else 0" but it goes wire frame when the communications are lost.