FactoryTalk View ME - Calling DISPLAYS

Bgc1369

Member
Join Date
Aug 2017
Location
Illinois
Posts
8
I have a display that I can't find out where it is being called by.
is there a "Display tree" that shows where each display is being called by?
I am developing SCADA screens on a PC that will show the same screens as the HMI has. and I can't find out where some of the screens are being called from.
Any help is appreciated. Thanks!
 
Check Global Connections>Display Tab. There are tag connections listed there that allows the PLC to open a display and to read a tag to see display open.

Replace Display Number- allows PLC to open Display with that number.
Remote Display Number- allows PLC to read Display number that is open.

Right click on a display > Display Settings > Display number. Each display should have a unique number for these connections to work correctly.
 

Similar Topics

As the title says, all of the client HMIs at the plant freeze up for about 5-10 minutes everytime I or a vendor make new routines or new tags in...
Replies
0
Views
18
Hello, I want to connect the Factorytalkview ME with rslogix500 to see the live response of HMI buttons in Rslogix500 ladder code . I am using PLC...
Replies
5
Views
108
Hello, I have a panelview plus that reads from 4 different PLC's. 2 of these used to be Micrologix PLC's and someone else went and updated them to...
Replies
3
Views
137
Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
Replies
0
Views
96
Hello all, I'm having trouble opening an application. After clicking open I'm prompted to login and after putting in username & password it...
Replies
0
Views
97
Back
Top Bottom