I have some questions about F0070 (profibusfault). These faults happen now and then...

I know that u may not send zero to the controlword, or you have profibusfault, so assuming that everything we send is correct...

What can trigger the profibusfault... do u we have bad networks, do we need amprolysers to check the network,

What do you guys think about this ?
 
According to the Micromaster Profibus manual Micromaster Profibus Optional Board (Entry ID 6586565)
this fault occurs because no set points were received from the Profibus communications board. It further suggests you check the network (connector, cable and master) and make sure the control word is valid (especially the set point). You could also power the communications board separately from the drive.

I had this problem once because I messed up something with one of the drive parameters. Unfortunately, this occurred too long ago for me to remember clearly. I do know that I had transferred and received the set point correctly and that I have the Profibus communications board powered up separately from the drive. I suggest checking the network and the drive parameters.

Is this a continuing problem related to this thread? http://www.plctalk.net/qanda/showthread.php?t=17526
 
Hi Combo.

Is there also a ProfiBus alarm on the PLC?

If you have another MM440 with ProfiBus module you could change the modules to check if the failure also changes or if it remains at the first drive.
If the failure changes you need a new ProfiBus module.

b r
ZIMBO
 

Similar Topics

I am experiencing an issue with the profibus modules on micromaster 420 drives. I would bet others are having the same problem so hopefully...
Replies
2
Views
4,066
Hi, I placed an MM440 as a slave of an S7 3152DP in a Profibusnetwork with 4 repeaters. Sometimes the error F070 occurs on the MM440. I checked...
Replies
1
Views
5,604
Hello Everybody, Recently we changed the gearbox which has different ratio than the original one on a motor which is controlled by Micromaster...
Replies
3
Views
1,915
Hello Experts I have to to make a backup of Siemens micromaster mm 440 with RS 485 to terminal 29&30. I use starter or drive monitor Do i need...
Replies
1
Views
1,223
:utoh: Hello, today tryed houres to connecting the micromaster 420 of my kaeser compressor to my laptop with the connection kit (MM4...