Hey Guys
Having some trouble again with message path, I thought I had these figured out but I've not been able to get this one working. I attached a diagram of what I am trying to do, and my best description of what I have.
I'm trying to MSG from a CompactLogix to CompactLogix through a ControlLogix backplane. I called Rockwell tech support and the guy I spoke to was not familiar and wasn't sure if what I was trying to do would even work. He suggested that I use the PLC in the ControlLogix rack as a data buffer.
Just wanted to check to see if anyone had experience with this, it seems like it should work but maybe its not possible.
4,192.168.1.10,1,0,2,192.168.0.20
4 - CompactLogix A (Port A2) - PLC A
192.168.1.10 - EN2Tin ControlLogix - Rack C
1 - Backplane - Rack C
0- Slot 1 L81 - Rack C
2- Ethernet Port
192.168.3.1 - CompactLogix (Port A1) - PLC B
Having some trouble again with message path, I thought I had these figured out but I've not been able to get this one working. I attached a diagram of what I am trying to do, and my best description of what I have.
I'm trying to MSG from a CompactLogix to CompactLogix through a ControlLogix backplane. I called Rockwell tech support and the guy I spoke to was not familiar and wasn't sure if what I was trying to do would even work. He suggested that I use the PLC in the ControlLogix rack as a data buffer.
Just wanted to check to see if anyone had experience with this, it seems like it should work but maybe its not possible.
4,192.168.1.10,1,0,2,192.168.0.20
4 - CompactLogix A (Port A2) - PLC A
192.168.1.10 - EN2Tin ControlLogix - Rack C
1 - Backplane - Rack C
0- Slot 1 L81 - Rack C
2- Ethernet Port
192.168.3.1 - CompactLogix (Port A1) - PLC B