anhkhoi
Member
Hi all,
I had trouble with commmunication between Mvi69 and mass flowmeter (micro motion-emerson).
I configured Mvi69 is master and mass flowmeter is slave using Rs485.
On mass flowmeters use floating point (2 registers 16 bits) for 1 data point. For example 0247-0248 for mass flowrate.
In Mvi card configured address for read this data point is 40248 (because of offset address is 40001).
but the data reading is not true, it jumped randomsly.
Data type on mvi69 is INT, so I not sure it can display floating point.
Anyone has experience on them? pls help me!