Cables to use with Prosoft MVI56E-MCM RS-485 2/3 wire

AREDA

Member
Join Date
May 2023
Location
UK
Posts
22
Hi all,

I wonder what's the best type of cable to use for RS-485 2 wire + GND
That is, Data+, Data- & GND

I know that Belden 9841 (not recommended for GND connection to use shield) / 9842 with AWG24

But my problem is, if we need to use intermediate terminals (e.g. for connection from one panel to another, and also to terminate unused core & screen), then AWG24 into screw terminals seems to be flimsy, and bigger conductor size would be better.
However, I'm reminded that the characteristic impedance of the cable for RS-485 is expected to be 120 ohm.
Frankly, I'm not expecting very long runs - maximum 30m or less.

Online it says the "GND" connection should not be ignored, especially if both systems don't have the same 0V reference, also the shield should not be used for the GND connection.

Thanks
 
Thanks Puddle
I do believe it works, it's just not ticking one box for me
in many sources and manuals, the 3rd connection "GND" is labelled optional, but it is said better to connect it where the 0V reference may not be the same at both ends. Many RS-485 ports would already offer the GND terminal.

Ideally, I'm looking for a 1.5 pair cable (also LSZH to compound the issue)

I think this cable is going to be ok
https://www.belden.com/products/Cable/Electronic-Wire-Cable/RS-485-Cable/9842LW

It's a trade-off, I don't like the small AWG24 when it comes to screw-terminals, but they do mention a wide range from AWG26 (or even AWG30, 0.2mm2) to AWG 12 (4mm2).
 
PROFIBUS DP physical layer is RS-485.
Maybe standard PROFIBUS cable would be suitable an easy to find amongst your suppliers.
Just an idea.
 
Thanks Alfredo
that seems to be also 2 conductors not 3.
I'm sure this means the GND conductor is not really needed as reported in some articles and as made available by some manufacturers.
 
Yes I understand about the shield, but the shield can go to Earth on one of the two ends (like you'd do with any homerun cable with screen); the "GND" terminal on the RS-485 interface should not be used for that, imo.
 

Similar Topics

Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
Replies
4
Views
215
Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
Replies
0
Views
121
Hi all, i have several Proface GT2400 terminals and i need to get the software and interface cables and i have several questions. I am assuming...
Replies
3
Views
178
Kindly, we connected electrical power, 3x380 vac, between a supply station and an electric cabinet, away 180 meters. The calculation software...
Replies
11
Views
903
Looking for some OEM or Industry guidance, due to mechanical damage some of our drive cables have been compromised. (Document to reference would...
Replies
5
Views
941
Back
Top Bottom