Hi ,

I have an Allen Bradley Powerflex 700 Inverter

It has a green power light ( led ) and under that has a status
Light ( led )

The Status ( sts ) light is a steady yellow whilst the drive is running
The manual indicates Paramater 211

I have checked this parameter and it shows
000 000 000 x 000 000

Does x indicate the fault ?

Many thanks in advance

Mike
 
No, that bit is reserved or not being used.

The zeroed bits indicate that none of those alarms is present.

I recommend to check parameters 211 and 212. When you find a bit set to “1” in 211 or 212, go check in the user manual what alarm that bit corresponds to.

Bye

Jose
 
Thanks Jose, I will check further

None of the bits are 1

It looks like the fault isnt showing
I will check parameter 212

Many thanks
 

Similar Topics

Got this new to me powered on today and have no main air and the only problem I have found is the f059 on the vfd. S1 has 24v, none on S2, and 48v...
Replies
10
Views
518
Greetings everyone, I know there is a way to programmatically set the date/time on a 750 series VFD (look up Rockwell automation sample code)...
Replies
1
Views
1,067
Can someone do me a huge favor and print these 2 Allen Bradley DNO files and email them to me? [email protected]...
Replies
1
Views
1,784
Hi all, Client with a pretty much brand new AB Powerflex VFD starting throwing Fault 17: Input Phase Loss this afternoon. Started doing some...
Replies
7
Views
9,744
We have a Powerflex 753 drive on a 192.168.1.X network that I can communicate with a Controllogix L71 with no issues on same network...
Replies
0
Views
1,459
Back
Top Bottom