Allen Bradley 193-EDN AverageFLA HMI setup

abarajas

Member
Join Date
Jun 2021
Location
ks
Posts
4
Hi everyone, I am currently working on a AB 193-EDN and i am trying to figure out this "Average %FLA", it keeps showing 70-75 but my clamp meter is showing about 4.9 on all three legs. We have the E1 overload set to 20amps trip, is this displaying a percentage or do i need to find a scaling for it. Trying to display it on a HMI for maintenance stuff.
1710465180628.png
 
Google search Publication 193-UM006A-EN-P
Chapter 4 (page 4-2)
This parameter reports the average motor current. The value is reported as a percentage of motor rated current (dial setting on the E1 Plus Overload Relay),and is reported in increments of 5
 