Adding Duplicate Standard PanelView (not Plus) to SLC 5/04 PLC over DH485

kloc5

Member
Join Date
Apr 2014
Location
St Louis
Posts
25
Hello,

We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in between. We would like to add another HMI that is an exact duplicate. What would be the best way to add this duplicate HMI to this machine? Is there a way to split the DH485 coming out of the AIC module to both? Is there anything in the HMI program that I would have to change on the second HMI to prevent communication issues? It has been a while since I've used PanelBuilder.

Thanks!
 
The "3" at the end of the part number indicates that this is a DH-485 protocol terminal with classic DH485 wiring. You must use the flash card or DH485 to upload and download; the RS-232 port on these is for printing only.

The 1761-NET-AIC has two RS-232 ports, and one DH485 combicon/screw-terminal trunk port.

Because you are connecting it to the Channel 0 RS-232 port of an SLC-5/04, you must be using one of the serial ports for the SLC, and the DH485 trunk port for the PanelView via an 1761-AS03 or -AS09 cable.

You will need another 1761-NET-AIC to connect an identical PanelView to this network.

If the new PanelView will be within 50 feet of the old one, you could link the two 1761-NET-AIC's with their unused serial ports.

The only configuration change you will definitely need to make is in the Configuration of the PanelView itself, so that it has a unique DH485 address.

There may be application reasons to change the application, like multistate pushbuttons that might conflict once there are two HMI terminals acting on the same PLC registers. But that's going to be application-specific.
 

Similar Topics

Hi, I need help adding a new interlock switch to an existing circuit. I have never done on the existing circuit. I did set it up on the...
Replies
6
Views
260
Hi all I’m looking at adding a RFID card reader to comfort panel pro , how do you set the rfid up can you connect to existing users and password...
Replies
0
Views
89
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
141
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
118
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
Replies
3
Views
195
Back
Top Bottom