3 wire RTD bolt on sensor wiring

bdoutney

Lifetime Supporting Member
Join Date
Aug 2011
Location
LI NY
Posts
92
There are 2 reds and a white wire in the sensor lead but the drawing shows the reds are in parallel. Does anyone know the purpose of this?
 
I believe the 3 and 4 wire RTDs are used for ambient temp compensation. Or maybe it was to compensate for lead resistance. I forget exactly which. But they are wired in parallel when attached to a device with two wire inputs.
 
The two red leads are connected at one end of the RTD resistor. The white lead is connectd to the opposite side of the resistor. The 2nd red lead is used to compensate for the resistance of the wiring, which improves accuracy. By measuring the resistance between the two red leads the resistance of the wires is measured and can be deducted from the total resistance. This leaves just the RTD element itself.
 

Similar Topics

Hello! I have RTD sensor with 4 wire and shield ( 2 red wire + 2 white wire + Shield) and I want to connect to 1734-IR2 module. But in the manual...
Replies
2
Views
1,438
Hi friends I got a PT100 Ohm RTD Automation Direct part number RTD0100-10-010-H .How in this case would I connect the RTD to a 3 wire device...
Replies
10
Views
4,812
Anybody else think that the notes (highlighted in red) is a misprint in the Siemens S7-300 manual for the 7KB02 analog input module RTD wiring...
Replies
5
Views
6,194
Is there any restriction to the lenght of RTD? If the RTD is 10m apart from my controller, should I need to order a RTD with 10m long of wire...
Replies
4
Views
4,387
Hi, just a short question... I'm using Allen Bradley 1771-IR to monitor a PT100 RTD (3-wire RTD). According to the manual, if I remove the A...
Replies
0
Views
3,440
Back