1794-IE8 Fast Analog Input Module

turbohamad

Member
Join Date
Jun 2009
Location
Multan
Posts
108
Dear Members;

We have Fluke 754 hart communicator. We have wired up three transmitters of Rosemount Model C3051 with this input module. But when i connected Hart it shows NO HART DEVICE FOUND.
while when we connect these transmitters to other analog input module which is not Fast Analog the hart reads the data.

Is it possible to read the data of transmitters at HART which is connected with Fast Analog Input?

what property of module i change?

Please help me

Regards
 
The 1794-IE8 is considered a "high density" and "non-isolated" analog input module, which also has a faster A/D converter because it's a relatively newer design than the original 1994-vintage 1794-IF4.

Are you using the ordinary 1794-IE8, or the 1794-IE8H, which has a built-in HART modem ?

Which exact part numbers of analog input modules work correctly with your external HART Communicator ?

If isolation between current-loop channels is a concern, of course go ahead and remove all but one of the devices from the module connections and see if your HART modem works on just one loop.

The input resistance of the 1794-IE8 is specified as 238 ohms. It is my understanding that a HART calibrator or modem should be put in series with a loop that has less then 250 ohms, instead of in parallel.

It is my understanding that the 1794-IE8H (with the built in HART modem) has an input resistance of 278 ohms, which makes it appropriate for the connection of a handheld like the Fluke 754 in parallel.
 
Last edited:
The Hart spec says minimum 230 Ohms of loop resistance; resistor goes in series in the loop. Wire resistance and AI input resistance count, as well.

If the AI has an integrated Hart modem, the Hart spec allows for a primary and a secondary Hart master. The handheld acts as a Hart master and an AI Hart modem would be a Hart master as well, so the Hart masters should play nice together.

One would think a Hart AI card would have an input dropping resistor that is suitable for Hart comm, but I’m too to check the product manual.

Hart AI threads are scarce. Please help us all and post your findings.
 
Dear Members;

We have Fluke 754 hart communicator. We have wired up three transmitters of Rosemount Model C3051 with this input module. But when i connected Hart it shows NO HART DEVICE FOUND.
while when we connect these transmitters to other analog input module which is not Fast Analog the hart reads the data.

Is it possible to read the data of transmitters at HART which is connected with Fast Analog Input?

what property of module i change?

Please help me

Regards

Spectrum Controls has a HART PointIO module that works pretty well.
 

Similar Topics

Hello all. I have a job to add a 1794-IE8 Card in slot 5 on an existing Flex IO Rack which uses a 1794-ASB communications module, which...
Replies
8
Views
3,009
I am trying to scale an analog input for 4-20ma. Rockwell's website says that 0-30840 are the proper numbers. But the unscaled input raw is...
Replies
4
Views
1,890
Hello, I would like to install a 1.25k-ohm potentiometer to a 1794-IE8. All I have is a 24VDC source. I noticed that the input ranges from...
Replies
8
Views
2,091
Hi All, I've probably programmed hundreds of 1794-IE8's over the years. The panel builder I'm working with has installed thousands of these so I...
Replies
3
Views
2,338
Hi, I am using an Analog Input Module - 1794/IE8 My Analog Input Module is configured for 0-20mA Unscaled Max = 31208 Unscaled Min = 6241.6...