Ok. We got a copy of the original connection diagram for this system and wired it up. According to the connection diagram:
The 10 HP 1200 RPM motor is the drive for the 15 KW motor Generator.
When the system is in LOW the four motors on the machine are connected to the 230 volt 3 phase line voltage. In HIGH mode the four motors are connected to the output from Generator. We test ran the system and to no one got maimed, killed, or electrocuted when we fired it up. So it all seems to work OK. Thanks to all for your help and info.
Robert
 
Rday, glad to hear it's in working order.

My curiousity is eating me up tho. If, as you state, the slow speed configuration has the four machine motors across a 230VAC 60Hz supply, then it follows that it will take more than 60Hz to acheive a higher speed.

It seems to me, then, that the alternator driven by the 25hp motor must produce a higher frequency than 60Hz and probably a higher voltage as well, assuming the machine motors are expected to maintain their full torque in the high speed mode.

It appears from the earlier motor nameplate data that the 25hp motor is six pole giving it a full load shaft speed of 1150rpm. The alternator being shaft coupled to the 25hp motor would have to have more than six poles to produce more than 60Hz but that is not apparent from the nameplate given.

Hmmmm! Curiouser and curiouser! Never seen anything remotely like this before!
 

Similar Topics

We have an old liquid ring vacuum pump sitting in the parts area, and its been there for years. I got curious about it, was looking at it, and the...
Replies
3
Views
2,134
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,628
I don't run a UL panel shop or do UL designs, but I try to keep my designs UL friendly because several times I've had to have it inspected before...
Replies
4
Views
2,451
have a question. Hope i can ask it so it makes sense. Have a gear motor that is rated at 650 lb_in that turns 47 RPM at max speed. Need to use...
Replies
7
Views
2,118
I have a typical motor that can be wired for 230/460 but is also rated for 208VAC operation. It has a typical 1.15 service factor. If I wire...
Replies
20
Views
6,994
Back
Top Bottom