LDT for hydraulic cylinders

ZBTB

Member
Join Date
Aug 2008
Location
NC
Posts
1
Hello, I am raising and lowering a platform with four hydraulic cylinders with a height tolerance +/- 1mm. I was looking for the best possible solution for an LDT, and if anyone would recommend using a Siemens SM334 analog I/O module or an SM335 fast analog I/O module for processing the feedback from the LDT. Any suggestions would be appreciated.
 
The easy way.

http://www.mtssensors.com/ and
http://www.balluff.com

I would recommend one of these hydraulic motion controller
http://www.deltamotion.com/products/motion/rmc100/index.php
You it costs more but you will save so much time because commands like SyncMoveAbs, SyncMoveRel and SyncStop are built in which allows you to keep your axes synchronized. It has graphing that will allow you to plot the positions, velocities etc of the actuators real time and programming capability that allows one to synchronously move 4 axes in just one command.

I prefer SSI rods because they don't drift as much as the analog rods do. The SSI also provides feedback at regulator intervals which is necessary for fine velocity control. Analog data is asynchronous to the motion controller. One can easily get 5 micron resolution which allows for more accurate speed estimates.

If you use the motion controller you may not even need the PLC.
Just add the HMI of your choice. Red Lions work well. If you decide you do need the PLC you can communicate with the motion conroller using Profibus DP to transfer up to 32 32 bit registers back and forth which is probably many more than you need.

What will make your project more 'interesting' is the tuning. Auto tuning makes life easy but that ususally can't be done unless the actuators can be moved separately.

Note, I sell the controllers but it is the best solution for what you want to do. I don't see how you will maintain 1mm with PID control unless you are moving, accelerating and decelerating very slowly. The motion controller includes things you probably haven't even thought of.

One more note. There are on-line training classes and controllers. The training classes don't cost that much and you will definitely save the cost of training by reducing the time it takes to set up a system. A four actuator project should take no more than 4 hours to get going one the wiring and plumbing is done right.
 
I second what Peter said.

I like the MTS SSI sensors the best however I have used the Balluff. I have seen some from Turck that looked good as well but have never used them.

I am using RMC controllers with my Siemens PLC's. They have a Profibus option for all their controllers. You may also want to check out their online forum.

http://forum.deltamotion.com/index.php
 

Similar Topics

Hello everyone, I'm reaching out for assistance regarding a project I'm currently working on. Specifically, it involves a hydraulic system with...
Replies
7
Views
446
Hi All, I could do with some advice on a hydraulic control system. It is necessary for me to accurately position a vertical hydraulic ram with...
Replies
34
Views
2,007
Hi, I am about to start a project controlling a hydraulic ram using a Siemens S7-1200 controller. It will need to be quite steady control, by...
Replies
1
Views
775
Good Evening Everyone, I am attempting to monitor the level of hydraulic fluid in a tank. The tank is 50 gallons. For insurance purposes we need...
Replies
16
Views
4,221
Hi I have an electro hydraulic valve with coil resistance 22 ohms that takes as +/-12V DC input with 40Hz dither superimposed. The valve controls...
Replies
7
Views
2,559
Back
Top Bottom