EX260 Ethernet/IP slave connection problem

Auotor

Member
Join Date
Sep 2021
Location
Russia
Posts
1
Hello there. I have bougth a SMC EX260 SEN-1 ethernet/ip slave and i want to control it from windows PC (with Modbus TCP may be?). Is it possible?
When i connected it to my PC the NS bulb is green flashing , which means , that "Connection is not established" and it is recomended to check master, but i don't have Ethernet/IP master at all. It is also reccomended to use RSLogix 5000 program to configure device, but i think it's about configuring master, not PC.
Is there any sugestions to solve my problem? I'm a begginer. Thanks.
 
Welcome!

No, you can't use it with ModBus. There are ModBus variants you would need to purchase instead.

There are resources (EDS, sometimes AOP) available for the EX range on the SMC website (USA site is best), but these are for adding to a Compact or Control Logix using Studio 5000.
 

Similar Topics

Hello resident geniuses, Working on a new project that was initially slated to have a CompactLogix, but due to lead times the PM made the switch...
Replies
6
Views
2,300
Hi everyone, We are having Fanuc 16 i CNC system. I need to interface SMC ex260 SEN-1 ethernet valve module with the CNC . Does anyone know the...
Replies
0
Views
370
Has anyone successfully set up communications to a SMC EX260-SEN1 from a MicroLogix 1400 using MSG instructions? They are Ethernet/IP and from...
Replies
4
Views
2,061
Hi all I am working with a SLC 5/02 and having trouble getting online with it. I am using a 1747-UIC adaptor which allows for USB>serial and...
Replies
8
Views
45
Hello guys i'm working with an s7 1200 plc with an ET 200S expansion module. The problem is that i can't find the plc when searching in the...
Replies
1
Views
107
Back
Top Bottom