I have a PLC5-40 with 1771-IL card. I need to change one of the channels from its current configuration of 0-5vdc|0-20 ma to the new required configuration of 1-5vdc|4-20ma. I made the change and accepted the edits but then it asked me if I wanted to download the I/O channel change. Is this a PLC download? The PLC is live now and if its a download I would shut down various equipment. The documentation is not clear what is going to occur if I answer yes to this and its not clear if I have to do it. (its a card in the local chassis).
 
Hi, welcome to the forum!! Yes it will shut down your process (PLC goes into program mode on a download) and it will probably ask/tell you that some of your data will have changed, which would be the analog you have configured at the previous voltage/current in the logic or data tables. I used to do a lot on PLC 5 but haven't in a while. You might look at the manual for that particular card and it would tell you the sequence involved in changing channel configuration either on or off line. Hope this helps. That literature is available on line in PDF to look at and download.
 

Similar Topics

I have a PLC5-40 with 1771-IL card. I need to change one of the channels from its current configuration of 0-5vdc|0-20 ma to the new required...
Replies
0
Views
1,415
Hello, I have several PLC projects with elaborate hardware configurations and now at field commissioning I see that some of the order numbers are...
Replies
6
Views
3,042
Hi I am learning PLC programming and recently wrote on PLC program for a small project. I wrote code in vmware and downloaded in PLC later on...
Replies
2
Views
2,081
Hi I am trying to increase the baud rate of a 1756 DHRIO series B module from 57.6kbps to 230 kbps. You can not do it through switch settings or...
Replies
1
Views
5,003
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
265
Back
Top Bottom