Quote:
Originally Posted by daba View Post
Having said that, I've re-read your original post, and admit to being a little confused as to what you actually do want.
Hi Daba,

thank you for your suggestion.

We are developing modules (motor, valves, etc.) under S88 standard. the aoiSystem module needs to pass the last scan time (if the process task is continuous type) or scan time (if the process task is periodic type) to tag stsData.stslastScanTime.

in valve module, valve traveling time counts up by adding last scan time (stsData.stslastScanTime). i.e. pvtTravelTmr := pvtTravelTmr + sysData.stsLastScanTime; and this is the purpose why we need to differentiate between coninuous and periodic (in this case, periodic and event are the same, so we don't need to differentiate periodic and event).

Regards

Simon
  Reply With Quote
Old August 19th, 2009, 08:00 AM   #17
Brownhat
Member
United States

Brownhat is offline
 
Join Date: Mar 2007
Location: MN
Posts: 139
If you are using the value stsData.stslastScanTime to total up valve travel time, or motor run time, you will need more than the Program or Task scan time, you will need the total elapsed time since the previous scan. Maybe you should be capturing the CurrentValue from the WALLCLOCKTIME and finding the difference every execution. This should give you the total elapsed time since the last scan in microseconds.
  Reply With Quote
Old August 19th, 2009, 09:35 AM   #18
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,881
My thoughts entirely, Brownhat.

Simon, you will never know the actual "valve travel time" from your calculations, only the time interval between writing the output tag to the database, and receiving the open or closed feedback into the database. These are factors outside your control, and as such ought to be discounted for s88.

Let's say your Output and Input modules RPI settings are 20mS (default value), then without using Event tasks driven by Input data change, and IOT instructions to update outputs immediately, your timing will be +/- 40mS. And as you'll be writing output tags at different times within your program scan, you'll need IOT instructions after every output is turned on or off. Just think of the loading on the I/O network this will cause.

IMHO this time is inconsequential to an actual valve, whose "repeatability" will be far greater than that.

Methinks you are trying to take things too far.

Last edited by daba; August 19th, 2009 at 09:48 AM. Reason: explain
  Reply With Quote
Old August 19th, 2009, 03:36 PM   #19
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,001
This should work for returning the elapsed time between execution of any continuous or periodic task, and it will work for event tasks as long at less than 35 minutes elapses between events. The elapsed time is in microseconds. This is the elapsed time between two scans of the task, not the scan time of the task. If you know this then does it really matter if the task is periodic or not?

It uses the task start time and saves this value as a reference time to compute the elapsed time the next time the task starts. It doesn't give you the configured period for a periodic task (besides, you know how to get that), but it does give the actual period.

This method relies on the fact that the CLX performs unsigned subtraction between numbers when overflow and underflow occurs. If it were any other AB plc then you would have to emulate unsigned subtraction which isn't difficult, but since the CLX does it for us, we won't bother. Also, if you might use the code in an event task where the time period is greater than 35 minutes then you are going to have emulate unsigned subtraction with a borrow from the MSW, which can be a real PITA.

//Data[4] is a DINT array
//Get the task start time as a 64 bit time value in microseconds.
GSV(Task,THIS,StartTime,Data[0]);
//On the first scan no reference time exists so we cannot calculate an elapsed time
IF (NOT S:FS) Then
//Compute the elapsed time. We will only concern ourselves with the least
//Significant DINT of the time reference and we will treat it as unsigned.
//If overflow/underflow occurs the result will be the result of an unsigned subtraction and will still be correct.
//Data[3] contains the time between two successive starts of the task in microseconds
Data[3] := Data[0] - Data[2];
End_If;
//Save the task start time as a reference for next time the task starts. Ignore MSW in Data[1]. We will only bother with the LSW.
Data[2] := Data[0]

I tested this on a CLX this morning and let it run through two rollovers of the LSW of the time reference.

It should give you what you need - but I agree with Daba that because of the asynchronous nature of your IO that the true actual valve travel time will be different. If you need to have accurate valve positioning then a valve position transducer is the way to go.
__________________
True craftsmanship is only one more power tool away.

That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.

Last edited by TConnolly; August 19th, 2009 at 03:42 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Logix 5000 PID Instruction in a COntinuous Task plcnovel LIVE PLC Questions And Answers 29 August 13th, 2007 12:11 PM
RSLogix 5000 FB Totalizing - Periodic or Main Task BillRobinson LIVE PLC Questions And Answers 2 May 24th, 2007 11:35 AM
rslogic500 /controllogic 5500 mgomezov LIVE PLC Questions And Answers 23 June 14th, 2006 11:36 PM
RSLogix 5000 V15 Features Samneggs LIVE PLC Questions And Answers 18 April 20th, 2006 05:45 PM
PIDE's in periodic tasks RSLogix 5000 BENNY LIVE PLC Questions And Answers 18 August 25th, 2005 11:06 AM


All times are GMT -5. The time now is 05:32 AM.


.