Guys, I have a seimens UNIOP operator screen. It has locked up, ive done the obvious (checked comms plug and powered down) but it just sits their with the "comms" led winking at me and no buttons work. Its plugged into the RS422 port of a Texas Instrument PLC. It has worked fine for months. Any suggestions??
Thanks in advance
 
Depending on the model, EXOR has a number of tricks like the one Hazey described to bring the unit up in confguration mode and such. For example, if you tap the screen once per second during a power cycle, the application won't load and instead the unit will come up ready to download a new configuration. EXOR's tech support isn't quite as good a it used to be, but they are still very knowledgable and helpful. Have you tried them at exor-rd.com?

If the comms LED blinks it usually means that the serial link to the PLC is dead. Check the PLC status, check for loose wires, etc. Do you have multiple pages on the unit? If so, can you change screens? Yes to both means that the EXOR itself is probably OK. Can you switch to status mode? Have you checked the diagnostics messages on puwer cycle? Have you verified the comm port on the EXOR is working by testing with another device? These are all troubleshooting techniques that identify where the problem resides.
 

Similar Topics

Dear Friends, One of my client got two old Uniop HMI 1- eTop306 HW Version 768 2- eTop 05 HW version 3882 I need software to upload/download...
Replies
1
Views
1,481
Good afternoon everyone, Got a client with an oooold PLC/HMI setup. PLC is a SLC 5/02(logix 500 yes?) But for the HMI I've not a clue what...
Replies
2
Views
7,572
Hello All, I've a UNIOP panel (EK-04) VER. 4.40,when i checked the plc status from its (SYSTEM) menu, the status says (PLC.......COMM ON 00) as...
Replies
2
Views
1,705
Hi All, we have a UniOp HMI ER-25T-0021-F display currently connected to a Allen Bradley SLC 5/03. We are using the DH485 port on the SLC to...
Replies
1
Views
2,475
Has anyone ever had experience of data communication between a uniop hmi and the fanuc cpu374? I have setup the protocol in jmobile, however do i...
Replies
8
Views
2,424
Back
Top Bottom