I will give you an example : All my experience is based on Rockwell Software if you change the name of a client pc you will no be able to log on again on the SCADA server.
 
WinCC Advanced does not have Client/Server functionality.

The only bad effect I can imagine that you can no longer remotely load a PC Station that is combined WinCC + Simatic Net installation.
WinCC will continue to operate independent of its own Name.

Transferring a WinCC project uses the IP Address.

But transferring a Simatic Net project uses the Device Name, so that is the scenario that could be affected.
 
Here is another potential (indirect) bad consequence.

If there is some network monitoring system in place, changing any device name can generate false errors.
This includes the Diagnostics of Siemens canned system functions, especially if the Topology is fully configured, i.e. all devices, cables, ports, names etc.
This also includes the Diagnostics programmed into the HMI programs on other WinCC panels or HMI stations.

Everything will continue to operate, but there might be false errors.
 

Similar Topics

Hoping someone can give me some guidance or confirmation of what I need to do. We have a FactoryTalk SE program that I need to change the IP...
Replies
2
Views
65
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
167
Greetings I have a problem, my system is the following: wincc v8.0 (demo), logo8.3, abb m2m analyzer. I created some pages to display the...
Replies
0
Views
61
We had one go down. we have a new one. Their emergency Number don't work. The Model is TLSA046AAH-330N01-007 A catalog says we need software TET...
Replies
2
Views
170
“The HMI files we cannot open—they were saved in V13—we do not have that—I cannot restore file –please have them save in V11 and send them back to...
Replies
4
Views
173
Back
Top Bottom