Time-out error on NS8

vegarjegar

Member
Join Date
Jan 2014
Location
Norway
Posts
3
Hi there!

Would like to give my thanks to all the problemsolvers out there, this site have helped me alot!

I have a small problem though, that i haven't encountered before.

When i start up NS8, it stays black for 20 seconds (that's my retry count). After that it comes up with an error:

"Time-out error occurs while downloading by the following case:
-Disconnection of the connecting cable
-Stopped host
-Incorrect time-out period

Allocation Host: HOVEDPLS"


I have a CJ2M CPU 31 that is connected to a NS8 hmi with ethernet, no router between them.
I've tried everything when it comes to ip address, nodes, address table, etn host settings, ethernet settings on the HMI etc. I've also made the routing to the build in ethernet port (250 to network 1).

PLC's IP: 192.168.1.1
sub: 255.255.255.0
Done nothing else except the routing table (built in port 250 to network1)

NS8's IP: 192.168.1.4
Sub: 255.255.255.0
Network 1 Node 4
Added the plc and computers ip on the address table. Also added the PLC as a host.

I can connect to them seperately through ethernet. Can ping and download program to them.

There's one thing that i don't understand though. At Integrator, it says on the CJ2M-EIP21 that the network is (-)
but the node is (1) and unit is (1). Can this be the hickup? If so, what have I missed?


Regards
 
zlgo.jpg


Side note; when i upload the network from the PLC, i find 2 EIP21's with the same unit number
 
Last edited:
I forgot to use a cross-over cable when I'm directly connected through ethernet!

All good now:)

Edit;
And yes, the EIP21 couldn't be on network (-).
Somehow i have Ethernet/ip on unit 1, and Built in ethernet on unit 250. Made a new route through unit 1.
 
Last edited:

Similar Topics

Hi everyone, i have a Siemens S7-300 Cpu 314C-2 DP with several cards of i/o and servos my laptop has TIA version 16 and 17 loaded and...
Replies
4
Views
61
Hi guys, Im trying to set the real time clock in my Mitsubishi FX1N, but it shows this error ES: 01800001 I have good communication with...
Replies
3
Views
143
Hi, I am facing an error inside Omron Network Configurator. I have 2 PLC communicate each other using ethernet cable, send signal using Network...
Replies
2
Views
102
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
Replies
2
Views
107
I have a Sinumerik 828D control panel and its for a CNC machine, the problem is that it gives an error state 700027 tool turret state :S4...
Replies
0
Views
102
Back
Top Bottom